hhsting
Senior Member
- Location
- Glen bunie, md, us
- Occupation
- Junior plan reviewer
Sketch attach shows two diagrams A and B. Both show from multiple service disconnects GEC tap to gnd bus bar.
However, Diagram A shows from ground bus bar:
a.one GEC to steel,
b. another GEC to water pipe,
c.another GEC to rods
d. bonding Jumper to inter system bonding terminal.
While Diagram B shows from gnd bus bar:
a.one bonding jumper to intersystem bonding terminal
b. from gnd bus bar one grounding electrode conductor to steel and bonding jumper from steel to pipe and another bonding jumper from steel to rods.
Which of the two diagrams: Diagram A or Diagram B is in compliance with NEC 2014 section 250.64(D)(1)?
However, Diagram A shows from ground bus bar:
a.one GEC to steel,
b. another GEC to water pipe,
c.another GEC to rods
d. bonding Jumper to inter system bonding terminal.
While Diagram B shows from gnd bus bar:
a.one bonding jumper to intersystem bonding terminal
b. from gnd bus bar one grounding electrode conductor to steel and bonding jumper from steel to pipe and another bonding jumper from steel to rods.
Which of the two diagrams: Diagram A or Diagram B is in compliance with NEC 2014 section 250.64(D)(1)?