NEC 2014 section 422.31 lets say I have appliance. Following questions:

1. If the appliance has motor less than 1/8 hp and the engineer still wants to provide local disconnect then is that not code compliance?

2. If the appliance is less than 300va and no motor and the engineer still wants to provide local disconnect then is that not code compliance?
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
That is why it says "shall be permitted"
422.30 says the appliance has to have a disconnect.... if one wants to go beyond "minimum permitted" that's fine.

(
 