Hello All,
Can #2/0 CU wires be protected by a 200A main breaker?
#2/0 wires are OK for 200A service (ampacity wise) per 83% rule but per 240.4(B)(2), next size breaker is permitted only if the ampacity of the conductors does not correspond with the standard ampere rating of a fuse or a circuit breaker. And per table 240.6(A), 175A is a standard breaker so it seems that #2/0 wires can't be protect by a 200A breaker.
What do you think?
Can #2/0 CU wires be protected by a 200A main breaker?
#2/0 wires are OK for 200A service (ampacity wise) per 83% rule but per 240.4(B)(2), next size breaker is permitted only if the ampacity of the conductors does not correspond with the standard ampere rating of a fuse or a circuit breaker. And per table 240.6(A), 175A is a standard breaker so it seems that #2/0 wires can't be protect by a 200A breaker.