I have service equipment for mobile home elsewhere on the premises. So disconnecting means is provided within 30 feet of trailer.

1. Does the disconnecting means has to have fuse or can it be non fused?

Thanks
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
550.32 seems to cover that.

The service equipment shall be permitted to be located elsewhere on the premises, if a disconnecting means suitable for use as service equipment is located within sight from and not more than 9.0 m (30 ft) from the exterior wall of the mobile home it serves and is rated not less than that required for service equipment in accordance with 550.32(C). Grounding at the disconnecting means shall be in accordance with 250.32.
 

hhsting

Senior Member
Location
Glen bunie, md, us
Occupation
Junior plan reviewer
550.32 seems to cover that.

The service equipment shall be permitted to be located elsewhere on the premises, if a disconnecting means suitable for use as service equipment is located within sight from and not more than 9.0 m (30 ft) from the exterior wall of the mobile home it serves and is rated not less than that required for service equipment in accordance with 550.32(C). Grounding at the disconnecting means shall be in accordance with 250.32.

Where code says suitable for disconnecting means require fuse in disconnect?
 