I attended Mike's seminar in Seattle last month. We discussed all the errata that are coming out from NFPA. I seem to have lost some of those emails. Is there a web page where I can go to get all of the currently issued errata? NFPA is saying there are only 3..But I recall some 40 or so from the seminar.

Any help please since the two printed 2017 NEC I have a now questions???

Thanks

Steven
 
Where did you find the three errata? Forty sounds like an awful lot considering most people haven't even purchased the 2017 NEC yet.
 
Here are the two I see


1. delete the #1 informational note in 300.4

2. Update a reference in 840.3(G) to read as follows:840.3(G) Electrical Classification of Data Circuits and Cables. Sections 725.139(D)(1)and 800.133(A)(1)(b) shall apply to the electrical classification of Class 2 and Class 3 circuits in the same cable with communications circuits.
 
Here are the two I see


1. delete the #1 informational note in 300.4

2. Update a reference in 840.3(G) to read as follows:840.3(G) Electrical Classification of Data Circuits and Cables. Sections 725.139(D)(1)and 800.133(A)(1)(b) shall apply to the electrical classification of Class 2 and Class 3 circuits in the same cable with communications circuits.
There's a #2 in the first doc...
2. In Table 310.104(A), Moisture-resistant thermoplastic, add a missing “0” (zero) to the first entry in the “mils” column to read as follows:
[Pertinent part of Table, not quoted here]
 