NEC 2017 Section 225.36

Status
Not open for further replies.

hhsting

Senior Member
Location
Glen bunie, md, us
Occupation
Junior plan reviewer
I have outside feeder feeding building A. Right where conductors enter Building A would fused disconnect with fuses in it comply as disconnect per NEC 2017 Section 225.36 or not?
 

Dsg319

Senior Member
Location
West Virginia
Occupation
Wv Master “lectrician”
I have outside feeder feeding building A. Right where conductors enter Building A would fused disconnect with fuses in it comply as disconnect per NEC 2017 Section 225.36 or not?
Don’t have a 2017 on me. Can you post what 225.36 says?
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
Don’t have a 2017 on me. Can you post what 225.36 says?
In the 2014:

225.36 Type. The disconnecting means specified in 225.31
shall be comprised of a circuit breaker, molded case switch,
general-use switch, snap switch, or other approved means.
Where applied in accordance with 250.32(B), Exception
No. 1, the disconnecting means shall be suitable for use as
service equipment.

225.31 Disconnecting Means. Means shall be provided
for disconnecting all ungrounded conductors that supply or
pass through the building or structure.
 