NEC 2017 section 250.64(D)(1)

Status
Not open for further replies.

hhsting

Senior Member
Location
Glen bunie, md, us
Occupation
Junior plan reviewer
Please see attached sketch shows two diagrams. One left and one right.

The one left shows three service fused discos have GEC tap to ground bus and then one GEC goes to underground water pipe from which all electrodes are bonded.

The one right shows three service fused discos have GEC tap to ground bus and then individual GEC goes to grounding electrodes.


Which one is in compliant with NEC 2017 section 250.64(d)(1) in your opinion?

cd7f9f28d8291e795863553ad3d342e3.jpg
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
Both are compliant so long as the conductors are properly sized and properly located.
 