NEC 2017 Table 210.21(B)(3)

Status
Not open for further replies.

hhsting

Senior Member
Location
Glen bunie, md, us
Occupation
Junior plan reviewer
I am confused by NEC 2017 Table 210.21(B)(3). I have duplex 15A receptacle on one circuit.

The way I see it the circuit does not have receptacles rated over 15A so 15A breaker should be provided but then I see it could be 15A or 20A next row making breaker 20A.

I am not sure would breaker be 15A or 20A?
 

xformer

Senior Member
Location
Dallas, Tx
Occupation
Master Electrician
I am confused by NEC 2017 Table 210.21(B)(3). I have duplex 15A receptacle on one circuit.

The way I see it the circuit does not have receptacles rated over 15A so 15A breaker should be provided but then I see it could be 15A or 20A next row making breaker 20A.

I am not sure would breaker be 15A or 20A?
Duplex receptacle counts as 2 receptacles. :)

Yes, mutiple 15 amp receptacles can be installed on a 20 amp OCPD. If memory serves correctly, the only difference between a 15 amp duplex receptacle and a 20 amp rated receptacle is the face plate.

Breaker must protect conductor utilized.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
More than one 15 amp receptacle can be on either a 15 or 20 amp branch circuit.
 

hhsting

Senior Member
Location
Glen bunie, md, us
Occupation
Junior plan reviewer
Duplex receptacle counts as 2 receptacles. :)

Yes, mutiple 15 amp receptacles can be installed on a 20 amp OCPD. If memory serves correctly, the only difference between a 15 amp duplex receptacle and a 20 amp rated receptacle is the face plate.

Breaker must protect conductor utilized.

Then why is their 15A breaker for receptacles not over 15A in the table?


Sent from my iPhone using Tapatalk
 

xformer

Senior Member
Location
Dallas, Tx
Occupation
Master Electrician
Then why is their 15A breaker for receptacles not over 15A in the table?


Sent from my iPhone using Tapatalk
A 20 amp load placed upon the 20 amp receptacle should cause the 15 amp breaker to activate. Therefore the table requires receptacles on a 15 amp breaker to be no greater than 15 amp.
 