mwm1752
Senior Member
- Location
- Aspen, Colo
Sometimes the revised code just doesn't add up or I am not seeing the the interpretation correct.
230.71(B) basically eliminated - up to six service disconnecting means for a service disconnect "grouped in a single enclosure". There are conditions 230.71(A)(4) switchgear with up to six disconnects for the service disconnect is allowed as long as the disconnects are located in a separate compartment. Those 2 statements have me interpreting the separate compartments are for each disconnect and not attached to a buss side by side.
I believe 230.90(A) exc. 3 describes over current protection of service conductors in the case of 230.71(A)(4).
Now look in the Handbook Exhibit 230.23 & I see up to six service disconnecting means for a service disconnect "grouped in a single enclosure". The visual is very deceiving & when enforcing inspections in the field contractor rely on NFPA handbooks for clarity. I am thinking this was overlooked by NFPA and the illustration was not revised or maybe I am missing something here.
230.71(B) basically eliminated - up to six service disconnecting means for a service disconnect "grouped in a single enclosure". There are conditions 230.71(A)(4) switchgear with up to six disconnects for the service disconnect is allowed as long as the disconnects are located in a separate compartment. Those 2 statements have me interpreting the separate compartments are for each disconnect and not attached to a buss side by side.
I believe 230.90(A) exc. 3 describes over current protection of service conductors in the case of 230.71(A)(4).
Now look in the Handbook Exhibit 230.23 & I see up to six service disconnecting means for a service disconnect "grouped in a single enclosure". The visual is very deceiving & when enforcing inspections in the field contractor rely on NFPA handbooks for clarity. I am thinking this was overlooked by NFPA and the illustration was not revised or maybe I am missing something here.