NFPA appears to have added emergency disconnects into the mix for one and two family disconnects. The requirements for this equipment is:
1 - all service conductors shall terminate in disconnecting means. Same as 230.70(A)(1)
2 - installed in a readily accessible outdoor location.
The emergency disconnect can be the service disconnect, and as long as a nonfusable disconnect is used, the drop/lateral remains as service conductors. I am using the NFPA "NEC 2020 Analysis of Change" to help with creating a code change course for contractors during this Covid-19 shut down.
The wording NFPA AoC authors us for the NFPA 2020 NEC code statement "installed in a readily accessible outdoor location." is -- "installed & located on the outside of a structure." I cannot find anywhere in the NEC that an accessible location related to service disconnecting means has any distance restriction from a structure or even to mounted on the structure.
Further more if the intent is to have a disconnect on the structure, most likely it would be fused becoming the service disconnect, & feeders would enter the building.(in most cases).
Does anyone know in the NEC where it states the service disconnecting means has to be mounted on the structure or has a restriction to a lateral distance away which would eliminate the disconnect as the structure disconnect.
1 - all service conductors shall terminate in disconnecting means. Same as 230.70(A)(1)
2 - installed in a readily accessible outdoor location.
The emergency disconnect can be the service disconnect, and as long as a nonfusable disconnect is used, the drop/lateral remains as service conductors. I am using the NFPA "NEC 2020 Analysis of Change" to help with creating a code change course for contractors during this Covid-19 shut down.
The wording NFPA AoC authors us for the NFPA 2020 NEC code statement "installed in a readily accessible outdoor location." is -- "installed & located on the outside of a structure." I cannot find anywhere in the NEC that an accessible location related to service disconnecting means has any distance restriction from a structure or even to mounted on the structure.
Further more if the intent is to have a disconnect on the structure, most likely it would be fused becoming the service disconnect, & feeders would enter the building.(in most cases).
Does anyone know in the NEC where it states the service disconnecting means has to be mounted on the structure or has a restriction to a lateral distance away which would eliminate the disconnect as the structure disconnect.