NEC 2023, Art. 240 Overcurrent Protection. 240.2 Protection of Conductors.
New Text
240.2 Protection of conductors.
(A) Power Loss Hazard. … Short-circuit protection shall be provided.
(?) Current-Transformer Secondary Conductors. Conductor overload protection and short circuit protection shall not be provided for current transformer secondary conductors. An open current-transformer secondary circuit presents a high-voltage hazard.
(B) Overcurrent Devices Rated 800 Amperes or Less. …
Substantiation: Open CT secondaries can develop voltages of several thousand volts. This is a hazard to equipment and personnel. See https://www.nrc.gov/docs/ML1713/ML17137A031.pdf [Public Domain document] for example data.