NEC 2023 section 700.5(D) Redundant Transfer Equipment

anbm

Senior Member
Location
TX
Occupation
Designer
700.5(D) Redundant Transfer Equipment.
If emergency loads are supplied by a single feeder, the emergency power system shall include redundant transfer equipment or a
bypass isolation transfer switch
to facilitate maintenance as required in 700.3(C) without jeopardizing continuity of power.

According to the above code rule, if a building has a emergency generator that powers (1) emergency ATS (NEC 700) and (1) optional standby ATS (NEC 702),
the emergency ATS must be bypass isolation type, correct?
 