Originally posted by channing123:
all nec states is 20amp cir gfi protected within3 foot of edge of sink :roll: not individual branch cir
That sounds like an individual (dedicated) circuit to me!NEC 2005, 210.11(C)(3) Bathroom Branch Circuits. In addition to the number of branch circuits required by other parts of this section, at least one 20-ampere branch circuit shall be provided to supply bathroom receptacle outlet(s). Such circuits shall have no other outlets.
Again, per NEC 2005. It was clarified.Exception: Where the 20 ampere circuit supplies a single bathroom, outlets for other equipment within the same bathroom shall be permitted...