NEC 210.23 Lighting Branch Circuits

Status
Not open for further replies.

bp8822

Member
I am looking for help on NEC section 210.23. I have a situation where I would like to place a lighting branch circuit on a 40A breaker (non-dwelling unit application). The fixtures are fluorescent type. The code mentions heavy-duty lamp holders, but I am unsure how this applies to a fluorescent fixture. Has anyone run into this situation previously that could provide some insight?
 
I believe that heavy-duty lamp holders refers to HID lighting, I guess you could interpret "other utilization equipment" to mean lights. I am curious why not a smaller circuit?
 
The fixture is a six lamp T5HO fixture. I can only place 3 fixtures on a 20A circuit. Since I have approximately 40 fixtures in a single space, I was trying to eliminate the number of branch circuits for control purposes. I am going to have to use a contactor in any case.
 
bp8822 said:
I am looking for help on NEC section 210.23.

The code mentions heavy-duty lamp holders, but I am unsure how this applies to a fluorescent fixture.
210.23 does not apply, but rather 210.21(A).

The commentary (although NOT enforceable) following 210.21(A) states:
The intent of 210.21(A) is to restrict a fluorescent lighting branch-circuit rating to not more than 20 amperes because most lampholders manufactured for use with fluorescent lights are not of the heavy-duty type and are rated at 660 watts or 250 watts.
Branch-circuit conductors for fluorescent electric-discharge lighting are usually connected to a ballast rather than to lampholders, and, by specifying a wattage rating for these lampholders, a limit of 20 amperes is applied to ballast circuits.
Only the admedium-base lampholder is recognized as heavy duty at the rating of 660 watts. Other lampholders are required to have a rating of not less than 750 watts to be recognized as heavy duty. The requirement of 210.21(A) prohibits the use of medium-base screw shell lampholders on branch circuits that are in excess of 20 amperes.
 
Other than the code rule, what does the socket have to do with this issue when it is on the load side of a current limiting ballast?
Don
 
I think that the commentary makes this issue clearer for me. Although it seems that it would be easier to state something clearer in the code. I spent some time looking over the fluorescent fixture cutsheets, but I could not find any mention of the rating for the lampholder. I guess essentially though it doesn't matter since the lamps are connected to the ballast. Also I failed to mention earlier that this is a 120V branch circuit in case anyone was wondering...

Thanks for the input...
 
don_resqcapt19 said:
Other than the code rule, what does the socket have to do with this issue when it is on the load side of a current limiting ballast?
Don

Are you asking me, the OP or just throwing another log on the fire?
 
bp8822 said:
Also I failed to mention earlier that this is a 120V branch circuit in case anyone was wondering...
I was, and is it possible for you to change this? Many modern ballasts can accept a voltage range, even up to 277.

As for switching a large number of circuits, it can be easier and more economical to switch an entire panel with a contactor.
 