I just completed another job falling under the above codes and had an interesting observation. I have three ?" EMT's leaving a lighting control panel with 3 circuits each at 9 to 10 amps each. I opted to run a grounded conductor for each circuit rather than handle tie. These raceways are noticeably warm to the touch. Lets figure I have around 60A flowing on the conductors per raceway. Had I opted for one grounded conductor and ties I would be looking at 40A or less in each raceway.
I just found this interesting as the IECC wants me to conserve energy yet by my choice of application of the NEC I'm creating more heat, increasing the resistance, and wasting energy. I actually wasted wire also.