210.4- MWBC shall have means to SIMULTANEOUSLY disconnect all ungrounded conductors...so here we go....
Contractor installs a 12/3 MWBC, with BOTH ungrounded conductors terminated on a single 20A circuit breaker, which is actually listed for his two conductors (QO-120 breaker).
#1- His MWBC ungrounded conductors DO SIMULTANEOUSLY disconnect, with this setup.
#2- Obviously, neutral current can no longer cancel out, since both hots are now on Line 1, instead of Line 1 & Line 2. So 40 amps COULD possibly flow on his neutral conductor.
BUT, the 20 Amp circuit breaker limits the neutral conductor to only 20 Amps.
#3- Technically, by putting both ungrounded conductors on same breaker (which is listed for such install), he no longer has a MWBC.
This type of install will never fly in my jurisdiction and it didn't. Appropriate double pole circuit breaker was finally installed.
Opinions??
Contractor installs a 12/3 MWBC, with BOTH ungrounded conductors terminated on a single 20A circuit breaker, which is actually listed for his two conductors (QO-120 breaker).
#1- His MWBC ungrounded conductors DO SIMULTANEOUSLY disconnect, with this setup.
#2- Obviously, neutral current can no longer cancel out, since both hots are now on Line 1, instead of Line 1 & Line 2. So 40 amps COULD possibly flow on his neutral conductor.
BUT, the 20 Amp circuit breaker limits the neutral conductor to only 20 Amps.
#3- Technically, by putting both ungrounded conductors on same breaker (which is listed for such install), he no longer has a MWBC.
This type of install will never fly in my jurisdiction and it didn't. Appropriate double pole circuit breaker was finally installed.
Opinions??