As a plans examiner, I have and had required contractors to provide receptacles (GFCI) on the roof tops of commercial buildings that only have powered roof fans or ventilators on the roof, yet in many instances I have several contractors argue that the outlet is not required because the fans are ?Ventilation? equipment.
I have found that there are several interpretations to when these outlets are and are not required (i.e. just for units containing refrigerant and such), yet I believe the intent of NEC 210.63 is to provide an outlet for the service technicians who are conducting service on any rooftop HVACR, HVAC or HACR equipment that has power accessible to the unit from the rooftop, for when during servicing (i.e. drilling, cutting, refrigerant evacuation/recovery and other such operations that may require a power source), the technician may attempt to ?makeshift? available power in order to perform the maintenance or service.
Although one of Mr. Holt?s newsletters provides that this rule does not include ventilation equipment, I suggest that the 2003 ICC Mechanical Code be referenced for the definition of ?Heating, Air Conditioning and Refrigerant Equipment? (See ICC?s definitions for ?Air Conditioning?, ?Air-Conditioning Systems?, and ?Ventilation?), although I can concur with Mr. Holt?s article if the roof top equipment does not include an electrical source available to the technician (i.e. relief vents and such) to ?makeshift? an outlet from.
Also, please consider 210.63?s inclusion of Heating equipment. For example: A modular electric heater that is rooftop mounted, and used for tempering make-up air for installations requiring frequent air changes. These units are rated up to 235KW and 22,000 CFMs, depending on heating requirements. The heaters are intended for indoor or outdoor installations in commercial kitchens, factories, foundries and similar commercial and industrial occupancies, yet they have no refrigerant, yet I would require an outlet per NEC 210.63 to be installed for the stated reason above of the ?technician may attempt to ?makeshift? and out from the available power in order to perform maintenance (i.e. drilling, cutting and such)?.
Comments Please,
With Thanks,
Larry
(The following is an excerpt from Mr. Holts' newsletter concerning this subject):
210.63 Heating, Air-Conditioning, and Refrigeration Equipment Outlet
The words ?on rooftops and in attics and crawl spaces? and the exception were deleted so that this rule would coordinate with the mechanical code. This section now reads:
A 15 or 20A, single-phase 125V receptacle outlet must be installed at an accessible location for the servicing of heating, air-conditioning, and refrigeration equipment (HACR) on rooftops and in attics and crawl spaces. The receptacle must be located within 25 ft. and on the same level of the heating, air-conditioning, and refrigeration equipment. The receptacle outlet cannot be connected to the load side of the equipment disconnecting means... Figure 210?8 Author?s Comment: This rule does not apply to ventilating equipment.
I have found that there are several interpretations to when these outlets are and are not required (i.e. just for units containing refrigerant and such), yet I believe the intent of NEC 210.63 is to provide an outlet for the service technicians who are conducting service on any rooftop HVACR, HVAC or HACR equipment that has power accessible to the unit from the rooftop, for when during servicing (i.e. drilling, cutting, refrigerant evacuation/recovery and other such operations that may require a power source), the technician may attempt to ?makeshift? available power in order to perform the maintenance or service.
Although one of Mr. Holt?s newsletters provides that this rule does not include ventilation equipment, I suggest that the 2003 ICC Mechanical Code be referenced for the definition of ?Heating, Air Conditioning and Refrigerant Equipment? (See ICC?s definitions for ?Air Conditioning?, ?Air-Conditioning Systems?, and ?Ventilation?), although I can concur with Mr. Holt?s article if the roof top equipment does not include an electrical source available to the technician (i.e. relief vents and such) to ?makeshift? an outlet from.
Also, please consider 210.63?s inclusion of Heating equipment. For example: A modular electric heater that is rooftop mounted, and used for tempering make-up air for installations requiring frequent air changes. These units are rated up to 235KW and 22,000 CFMs, depending on heating requirements. The heaters are intended for indoor or outdoor installations in commercial kitchens, factories, foundries and similar commercial and industrial occupancies, yet they have no refrigerant, yet I would require an outlet per NEC 210.63 to be installed for the stated reason above of the ?technician may attempt to ?makeshift? and out from the available power in order to perform maintenance (i.e. drilling, cutting and such)?.
Comments Please,
With Thanks,
Larry
(The following is an excerpt from Mr. Holts' newsletter concerning this subject):
210.63 Heating, Air-Conditioning, and Refrigeration Equipment Outlet
The words ?on rooftops and in attics and crawl spaces? and the exception were deleted so that this rule would coordinate with the mechanical code. This section now reads:
A 15 or 20A, single-phase 125V receptacle outlet must be installed at an accessible location for the servicing of heating, air-conditioning, and refrigeration equipment (HACR) on rooftops and in attics and crawl spaces. The receptacle must be located within 25 ft. and on the same level of the heating, air-conditioning, and refrigeration equipment. The receptacle outlet cannot be connected to the load side of the equipment disconnecting means... Figure 210?8 Author?s Comment: This rule does not apply to ventilating equipment.