I don't see anything in 210.8(B) that says that. You could GFCI protect a feeder, and it would GFCI protect all the receptacles supplied by all the branch circuits that the feeder supplies. Of course, it may be too sensitive, as it would be looking at the sum of the leakage currents from all the branch circuits supplied (as pipe_bender just commented).The section requires the GFCI be located in the branch circuit.
But some elec. outlets > 20A are out available with GFCI protection, what is the solution?no. They will still require GFCI protection. The section requires the GFCI be located in the branch circuit. The G in LSIG is for ground fault protection of equipment. Not personnel. Their trip points are not the same.
I don't see anything in 210.8(B) that says that. You could GFCI protect a feeder, and it would GFCI protect all the receptacles supplied by all the branch circuits that the feeder supplies. Of course, it may be too sensitive, as it would be looking at the sum of the leakage currents from all the branch circuits supplied (as pipe_bender just commented).
Cheers, Wayne
GFCI protection exists for all of the requirements of 210.8. You might need to put them on a GFCI breaker.But some elec. outlets > 20A are out available with GFCI protection, what is the solution?
GFCI breakers are available thru about 60 amp (I think Siemens now offers a 100 amp unit), or you can purchase GFCI protection from manufacturers such as Littlefuse for higher amperage use.But some elec. outlets > 20A are out available with GFCI protection, what is the solution?
I was not, although it is on point. But basically unnecessary, as 210.8(B) has no language about the GFCI being located in the branch circuit. It just has to be at or upstream of the receptacle, so the receptacle is protected.Are you referring to 215.9?
50A GFCI breaker is not standard correct?Are you referring to 215.9?
I didn't see that. I always assumed that the GFCI requirement to protect receptacles would require it be present in the branch circuit.
GFCI protection exists for all of the requirements of 210.8. You might need to put them on a GFCI breaker.
50 amp GFCI breakers are available from most, if not all, manufacturers.50A GFCI breaker is not standard correct?
50A GFCI breaker is not standard correct?