Code Question: NEC 220.15 (2002)
load calculation. For fixed electrical heating ( baseboard(s)
This is a code question , not a wiring question.
New installation for fixed electrical heating
The main source of heating in this home is two gas furnaces . The fixed electric heater(s) ,
will be installed in 4 bedrooms as a supplemental source of if needed. 2 per room and 1 in the 4th bedroom. The units from what im told will not be on all the time.
NEC (2002) Art 220.15 Load calculations states ? shall be computed at 100% of the total connected load.
The total load for the fixed electrical heating is 3500 VA 240\3500 =14.5A.
The gas furnaces loads with motors etc total 2880VA
AC Load 6200VA
My question is where does this fixed electrical heating ( not on all the time ) figure into the load calculations.
I know that in the load calculations you choose the higher of the demands of AC or Heating, but I don?t think this is the case because the furnace(s) are the main heating source for the house and the AC system is the higher KVA of the both. My question is where does this fixed electrical heating ( not on all the time ) figure into the load calculations. I was thinking of fasted in place appliances . But you de-rate fasted in place by a 75% demand factor. NEC 220.15 states 100%. For the fixed in place space heaters Im not sure where this goes, Never had this situation before.
Not sure where to put this calculation. Im the only one on this job. The boss is out of town, the lead electrician is with him, and no one knows at the office.
Great community. First time here.
Steven,
JE98 , 2 years
load calculation. For fixed electrical heating ( baseboard(s)
This is a code question , not a wiring question.
New installation for fixed electrical heating
The main source of heating in this home is two gas furnaces . The fixed electric heater(s) ,
will be installed in 4 bedrooms as a supplemental source of if needed. 2 per room and 1 in the 4th bedroom. The units from what im told will not be on all the time.
NEC (2002) Art 220.15 Load calculations states ? shall be computed at 100% of the total connected load.
The total load for the fixed electrical heating is 3500 VA 240\3500 =14.5A.
The gas furnaces loads with motors etc total 2880VA
AC Load 6200VA
My question is where does this fixed electrical heating ( not on all the time ) figure into the load calculations.
I know that in the load calculations you choose the higher of the demands of AC or Heating, but I don?t think this is the case because the furnace(s) are the main heating source for the house and the AC system is the higher KVA of the both. My question is where does this fixed electrical heating ( not on all the time ) figure into the load calculations. I was thinking of fasted in place appliances . But you de-rate fasted in place by a 75% demand factor. NEC 220.15 states 100%. For the fixed in place space heaters Im not sure where this goes, Never had this situation before.
Not sure where to put this calculation. Im the only one on this job. The boss is out of town, the lead electrician is with him, and no one knows at the office.
Great community. First time here.
Steven,
JE98 , 2 years