My understanding of article NEC 220-60 is... if a building has air handler units (fans + compressors, condensers) to provide AC; And electric fan power boxes to provide electric heat. When we size the main service panel for the building, we only take the larger load among these two load + air handler fans load into our calculation.
My fellow mechnical man said I have to count both data into my calculation since even in winter time, some folks want to turn on the heat in one room and other want to turn on AC at anoother room, but if I count both data my panel size will be huge.
And I beleive there are no standard power factor that we can applies in this calculation to reduce electrical load. Anyone has any solutions? Actually, in the past, we have one project and the plan reviewer has rejected our project because he saw main switchboard calculation is overloaded even only 45A. If we only count electric heat load (larger load) + fans and take our AC load, we would pass. But I need to find a good reason to backup ourself.
Thannks!
My fellow mechnical man said I have to count both data into my calculation since even in winter time, some folks want to turn on the heat in one room and other want to turn on AC at anoother room, but if I count both data my panel size will be huge.
And I beleive there are no standard power factor that we can applies in this calculation to reduce electrical load. Anyone has any solutions? Actually, in the past, we have one project and the plan reviewer has rejected our project because he saw main switchboard calculation is overloaded even only 45A. If we only count electric heat load (larger load) + fans and take our AC load, we would pass. But I need to find a good reason to backup ourself.