Correct me if I'm wrong: 220.83 can't be used to size a service or feeder. It can only be used to check if the feeder or service is adequate for additional loads?220.82 would cover any new construction, where 100A is the minimum per 230.79 or 225.39. So the 100A is baked in already.
Whereas 220.83 covers existing dwelling units, which might have smaller supplies from before 100A became the minimum.
Cheers, Wayne
I would say yes.Correct me if I'm wrong: 220.83 can't be used to size a service or feeder. It can only be used to check if the feeder or service is adequate for additional loads?
The 220.83(A) and (B) calculation does not take the A/C or Heat into account. It makes no sense to me as to why, but it never has.I would say yes.
Now, since you've studied these sections more closely than I have, it seems like the only difference between 220.83 and 220.82 is that 220.83 gives a number 1200 VA smaller, is that correct? In that the 40% starts at 8 KVA instead of 10 KVA, so you get 60% * 2 KVA = 1200 VA less.
That assumes that it is implicit in 220.83(A) that you have to include the larger of the heating or cooling loads, even though it isn't explicitly stated, as to omit it would be implausibly inaccurate.
Cheers, Wayne
220.83(B) explicitly does consider A/C and Heat.The 220.83(A) and (B) calculation does not take the A/C or Heat into account. It makes no sense to me as to why, but it never has.
I should have typed "existing A/C or Heat." I agree with you that it should be considered.220.83(B) explicitly does consider A/C and Heat.
And while the language of 220.83(A) doesn't, it would be a violation of basic physics to ignore it.
Cheers, Wayne
Yes...and it also applies to all existing loads (including HVAC) in 220.83(A).The first sentence of (2017) 220.83(B) is "The following percentages shall be used for existing and additional new loads." And the subsequent table covers A/C equipment and Heating equipment.
So 220.83(B) explicitly covers existing HVAC.
Cheers, Wayne
Ah right, I missed that 220.83(A) would cover them under the "existing loads" category. But what's weird is by not breaking the HVAC loads out in 220.83(A), they would fall into the "first 8 kVA @ 100%, rest at 40%" category. Vs being taken at 100% (usually) per 220.82 or 220.83(B).Yes...and it also applies to all existing loads (including HVAC) in 220.83(A).