I have an inspector asking for a service load calculation on an existing dwelling and also individual panel calculations on the 200A and 150A main panels.
My question is about 220.83 (A). We completed an electrical installation for a new swimming pool so no additional AC or elec space heating equipment was added and its seems this article applies. We're required to use the 100% of the 1st 8KVA and 40% of the remainder for existing and new loads which shall include: general ltg., small app. and the nameplate of all appliance fixed in place or located on a specific circuit, ranges, dryers and water heaters.
Am I to include nameplates of air conditioning equipment as an appliance fixed in place since they don t specifically list AC equip? If so, should only use the larger load of AC and Heat or include the ac units and the heat pump and supplemental heat packs in the electric furnace?
it seems so but why include both AC and heat pump since only one would be on at the same time?
My question is about 220.83 (A). We completed an electrical installation for a new swimming pool so no additional AC or elec space heating equipment was added and its seems this article applies. We're required to use the 100% of the 1st 8KVA and 40% of the remainder for existing and new loads which shall include: general ltg., small app. and the nameplate of all appliance fixed in place or located on a specific circuit, ranges, dryers and water heaters.
Am I to include nameplates of air conditioning equipment as an appliance fixed in place since they don t specifically list AC equip? If so, should only use the larger load of AC and Heat or include the ac units and the heat pump and supplemental heat packs in the electric furnace?
it seems so but why include both AC and heat pump since only one would be on at the same time?