This came up in a discussion with another engineer today. Consider a building supplied by two outside feeders, both from the same remote 277/480V service. One supplies a 500 KVA transformer that feeds a 1600A, 120/208V distribution section. The calculated load is 800A. The other feeder supplies a 1000A, 277/480V distribution section with a calculated load of 500A.
NEC 225.30(C): Additional feeders or branch circuits shall be permitted where the capacity requirements are in excess of 2000 amperes at a supply voltage of 600 volts or less.
For NEC 225.30(C) do we handle each voltage separately? Do we add calculated loads without regard to voltage (800A + 500A = 1300A)? Do we use the the ratings of the distribution sections without regard to voltage (1600A + 1000A = 2600A)? Do we use the transformer secondary rated amps instead of the distribution section rating (1388A + 1000A = 2388A)? Do we use the transformer primary rated amps so both feeders are calculated at the same voltage (602A + 1000A = 1602A)? Or maybe something else? Is there a clarification from the CMP on what NEC 225.30(C) means?
For that matter, what does "capacity requirements" mean? Is that calculated load? Equipment rated amps? Calculated load plus 20% for expansion? Something else?
Thanks in advance for any comments.
NEC 225.30(C): Additional feeders or branch circuits shall be permitted where the capacity requirements are in excess of 2000 amperes at a supply voltage of 600 volts or less.
For NEC 225.30(C) do we handle each voltage separately? Do we add calculated loads without regard to voltage (800A + 500A = 1300A)? Do we use the the ratings of the distribution sections without regard to voltage (1600A + 1000A = 2600A)? Do we use the transformer secondary rated amps instead of the distribution section rating (1388A + 1000A = 2388A)? Do we use the transformer primary rated amps so both feeders are calculated at the same voltage (602A + 1000A = 1602A)? Or maybe something else? Is there a clarification from the CMP on what NEC 225.30(C) means?
For that matter, what does "capacity requirements" mean? Is that calculated load? Equipment rated amps? Calculated load plus 20% for expansion? Something else?
Thanks in advance for any comments.