If a service to a residential house, on its load side supplies a feeder to an adjacent house or structure and the second house uses its inside subpannel as the first point of its disconnecting means NEC 225.31 and code says the maximum number of disconnects for the supply is six or
((( is limited to "six circuit breakers mounted in a single enclosure" )))
Obviously nec is cannot be counting the branch circuit breakers for this single sub pannel enclosure because more than 6 branch circuits would be needed.
Im sure they are referring only to the feeder disconnects but the necs choice of wording is erroneous when they say that such a house or structure:
"can be fed by no more than one feeder and must terminate into a single enclosure with no more than 6 breakers"
And if this is the case doesnt the main subpannel breaker serve also as the supply disconnect without having a dedicated pull switch to serve this?