s.d. cronk
Member
- Location
- Ohio
NEC 230.2c1 states that "additional services shall be permitted where the capacity requirements are in excess of 2000 amperes at a supply voltage of 600 volts or less"
A debate has occurred here in regards to the reference of "capacity requirements".
Does this mean that the first service will need to have a capacity in excess of 2000a and thereby allow a second service to "pick up" the remaining load that would be in excess of the 2000a?
Or does it mean that the combined service capacity will be in excess of the 2000a and thereby allow you an additional service and permit you to separate the loads as you desire, such as two services of 1200a each?
Or does it mean that the building has a calculated load in excess of 2000a and thereby allow two services consisting of either of a 2000a for the first and a second service for the remaining or two services of 1200a each for a total that would exceed the 2000a benchmark?
Or are all three convoluted amongst themselves and we are completely off base?
Thoughts?
A debate has occurred here in regards to the reference of "capacity requirements".
Does this mean that the first service will need to have a capacity in excess of 2000a and thereby allow a second service to "pick up" the remaining load that would be in excess of the 2000a?
Or does it mean that the combined service capacity will be in excess of the 2000a and thereby allow you an additional service and permit you to separate the loads as you desire, such as two services of 1200a each?
Or does it mean that the building has a calculated load in excess of 2000a and thereby allow two services consisting of either of a 2000a for the first and a second service for the remaining or two services of 1200a each for a total that would exceed the 2000a benchmark?
Or are all three convoluted amongst themselves and we are completely off base?
Thoughts?