NEC 230.6 Service Conductors - Outside a Building
Npstewart
Im hoping to get some opinions on NEC 230.6. I have a situation with a meter on the ground level of a residential building, and the main service disconnecting means would be on the exterior (2nd level) about 15 feet away +/- on an exterior service platform with permeant ladder. The intent is to get the service disconnect above flood.
Being that the service conductors never actually enter the building, and instead are routed on an exterior wall after the meter, would these conductors be considered "Outside the Building"?
230.6 Is below but I feel as though this section is mostly applicable or written for cases when the service conductors pass through the exterior footprint of the building.
Conductors shall be considered outside of a building or other structure under any of the following conditions:
  • (1) Where installed under not less than 50 mm (2 in.) of concrete beneath a building or other structure
  • (2)Where installed within a building or other structure in a raceway that is encased in concrete or brick not less than 50 mm (2 in.) thick
  • (3)Where installed in any vault that meets the construction requirements of Article 450, Part III
  • (4)Where installed in conduit and under not less than 450 mm (18 in.) of earth beneath a building or other structure
  • (5)Where installed within rigid metal conduit (Type RMC) or intermediate metal conduit (Type IMC) used to accommodate the clearance requirements in 230.24 and routed directly through an eave but not a wall of a building
Yes, since they're physically mounted to the outside of the building.
I've wondered if there is a code section that actually states explicitly that the service conductors must be run on the outside of the building or is it merely implied by some other section. :unsure:
I think this is the only rule that applies to service conductors inside the building.
230.70(A)(1) Readily Accessible Location.
The service disconnecting means shall be installed at a readily accessible location either outside of a building or structure or inside nearest the point of entrance of the service conductors.
It's funny becuase we often speak about running service conductors only on the outside of the building yet there is no direct wording in the NEC that says that it's required. We can infer it being required by the section that you've posted and by the list of installations in 230.6 that are considered outside of a building.
It would be much clearer if 230.6 had direct wording stating that service conductors can only be run on the outside of a building.
My initial take on this is that these would be considered "Overhead Service Conductors" and therefore cannot be "Readily Accessible", per NEC 230.24. Seeing how these conductors are leaving the meter and travelling to the disconnect, wouldn't they essentially be "Overhead" at that point?
Even though the feed from the transformer to the meter is "Underground", when they leave the meter to travel to the service disconnecting means they're essentially "Overhead". Basically, what I'm saying is that the utility meter is just an in-line device and the NEC makes no distinction before or after the meter.
Question:
In my example, if we moved the Electric meter to the second level but travelled along the exterior wall horizontally and vertically to get to the meter then this would likely be a code violation, correct? So why is it any different if the meter is on the ground level?
They don't meet the definition of that term in Article 100. Overhead service conductors are the same as service drop conductors except that the overhead service conductors are on the load side of the service point, and service drop conductors are on the line side of the service point.
You can run the conductors anywhere and as far as you want as long as they are on the exterior of the building. I see no violation.