Hello, I'm trying to decipher if an installation meets NEC 2020 Art 230.70. Both houses were completed in Florida in late 2021.
One house has a Square-D meter/panel on the outside with the panel clearly marked "Emergency Disconnect" with a main breaker inside as well as a 2-pole breaker which I haven't identified the use. Maybe for whole house surge protection? The distribution panel located in the garage does not have a main breaker.
Second house does not have an Emergency disconnect outside and has a main breaker on the panel inside.
I understand 230.70(A)(1) requires the service disconnect to be in a readily accessible location. I'm trying to determine 2 things.
1. Is the 1st house code compliant missing a main breaker on the panel? Can the Emergency disconnect serve duel purpose?
2. Is the 2nd house code compliant not having a service disconnect on the outside of the house? Can the main breaker being inside the garage be considered Emergency disconnect?
Neither seem correct based on Figure 230.1 in the 2020 Code.
Thank you in advance,.
One house has a Square-D meter/panel on the outside with the panel clearly marked "Emergency Disconnect" with a main breaker inside as well as a 2-pole breaker which I haven't identified the use. Maybe for whole house surge protection? The distribution panel located in the garage does not have a main breaker.
Second house does not have an Emergency disconnect outside and has a main breaker on the panel inside.
I understand 230.70(A)(1) requires the service disconnect to be in a readily accessible location. I'm trying to determine 2 things.
1. Is the 1st house code compliant missing a main breaker on the panel? Can the Emergency disconnect serve duel purpose?
2. Is the 2nd house code compliant not having a service disconnect on the outside of the house? Can the main breaker being inside the garage be considered Emergency disconnect?
Neither seem correct based on Figure 230.1 in the 2020 Code.
Thank you in advance,.