I have a Eaton 400 amp HP404040SHF W/split mains in Riverside County California.
I'm using the second sub breaker @ 150 amp. Back feed only from solar and 15kw batters. (grid tied)
230.71(B)
In general, a service should have a single disconnecting means.
However, one set of service entrance conductors is permitted to
supply two to six service disconnecting means in lieu of a single
main disconnect. Both single-occupancy and multiply-occupancy
buildings can be provided with one main service disconnect or up
to six main disconnects for each set of service-entrance conductors.
Conductors from renewable energy sources, such as photovoltaic
systems and wind generators, are feeder conductors.
Would this still be a non-compliant install.
I'm using the second sub breaker @ 150 amp. Back feed only from solar and 15kw batters. (grid tied)
230.71(B)
In general, a service should have a single disconnecting means.
However, one set of service entrance conductors is permitted to
supply two to six service disconnecting means in lieu of a single
main disconnect. Both single-occupancy and multiply-occupancy
buildings can be provided with one main service disconnect or up
to six main disconnects for each set of service-entrance conductors.
Conductors from renewable energy sources, such as photovoltaic
systems and wind generators, are feeder conductors.
Would this still be a non-compliant install.