I am checking a project that involves the installation of a new electrical service for a Waste Water Treatment Process. The service is from the secondary of a new 480/277V wye connected 1500 KVA utility transformer. The secondary conductors are routed underground to a new standalone 2000 amp circuit breaker located outdoors near the transformer. The breaker load side conductors are routed to a Process Motor Control Center via a service entrance rated transfer switch. The MCC serves only 480V three phase three wire loads.
Given that there are no 277V single phase loads:
1) Do we have to run the neutral to the Motor Control Center?
2) Are we bound by the requirements of 230.95?