Isaiah
Senior Member
- Location
- Baton Rouge
- Occupation
- Electrical Inspector
We have a large pad mounted transformer located outside the building. The secondary conductors are routed underground into the building that is only about 15 feet away. Inside the building, the cable stubs up and is routed overhead approximately 150 feet to a switchgear MCB where it terminates. This appears to be in compliance with 240.21(C)(4), but it just seems odd the code would allow this considering the 25 foot rule that precedes it - or am I missing something?
Sent from my iPhone using Tapatalk
Sent from my iPhone using Tapatalk