Shujinko
Senior Member
Installing a 75KVA transformer in a building. 480V delta pri - 480Y/277V sec, This will feed a panel with a 250A MCB that is more than 25' from the transformer secondary. My interpretation on 240.21(C) and 240.21 is that the Overcurrent protection device needs to be within 25' or 10' of the transformer secondary. It was brought to my attention that 240.21(C) is only talking about rules for not providing an OCPD on the transformer secondary. That once you provide an OCPD on the secondary you can put it any distance away from the transformer secondary. I was noting that 240.21, requires the OCPD to be located at a point where their conductors receive their supply except as specified in 240.21 A-H. So which one would be correct, OCPD within 25' (max) of secondary or no limit of OCPD distance from transformer secondary? Please provide applicable code citations.
My state in under NEC 2017.
My state in under NEC 2017.