AggieChris
Member
Based on 240.4 (b)-2 It appears that under normal circumstances, that the NEC allows the protection of a conductor to allow the conductor to be overloaded.
Assuming under 600 volts and ideal conditions ( completely continuous load, no derating, no voltage drop etc.)
If after the load calculations and conductor sizing calculations result in a 255 amps cable. Based on the conditions in 310.16 75 C terminations and insulation, I would pick a 250 MCM cable (like I said this includes the sizing factors i.e. 125% times full load).
The Protection sizing would result in a 255 amp protection( 125% times full load).
Based on 240.4(b) 2, I would then choose a 300 amp breaker, meaning that there is a possibility (between 255 and 300 amps) where the cable could be continuously overloaded without tripping the breaker.
SUMMARY:
Which takes precedent, sizing the conductor just for the load?
Or, sizing the conductor to ensure that the protection will always protect the conductor?
Conservative design says the latter, but it looks like the code may support the former.
Thanks,
Chris
Assuming under 600 volts and ideal conditions ( completely continuous load, no derating, no voltage drop etc.)
If after the load calculations and conductor sizing calculations result in a 255 amps cable. Based on the conditions in 310.16 75 C terminations and insulation, I would pick a 250 MCM cable (like I said this includes the sizing factors i.e. 125% times full load).
The Protection sizing would result in a 255 amp protection( 125% times full load).
Based on 240.4(b) 2, I would then choose a 300 amp breaker, meaning that there is a possibility (between 255 and 300 amps) where the cable could be continuously overloaded without tripping the breaker.
SUMMARY:
Which takes precedent, sizing the conductor just for the load?
Or, sizing the conductor to ensure that the protection will always protect the conductor?
Conservative design says the latter, but it looks like the code may support the former.
Thanks,
Chris