May I use #10 THHN with a 90 degree temp rating when there are 32 current carrying conductors in a conduit exceeding 24" in length supplying general receptacles in an office building and protect the conductors with a 20A circuit breaker.
Based on 310.16B the #10 wire is good for 40 amps and when I apply the 40% derating in 310.15 B2 I get a total ampacity of 16 AMPS.
My main question is on 240.4b (1) that applies when "not part of a multioutlet branch circuit suppying receptacles for cord and plug connected portable loads" Does 240.4 b (1) prohibit going up to a 20A circuit breaker on each hot conductor or am I reading into this too mutch.
Based on 310.16B the #10 wire is good for 40 amps and when I apply the 40% derating in 310.15 B2 I get a total ampacity of 16 AMPS.
My main question is on 240.4b (1) that applies when "not part of a multioutlet branch circuit suppying receptacles for cord and plug connected portable loads" Does 240.4 b (1) prohibit going up to a 20A circuit breaker on each hot conductor or am I reading into this too mutch.