Customer question:
"Long story short, the rPDUs we have 5KA rated breakers within them and I'm needing to reduce the fault current to an acceptable level from my busway.
To reduce fault current to a level acceptable for the PDU breakers, I planned to use a Bussmann fuse upstream. However, since the breakers are active components, I understand that NEC 240.86 requires a tested and listed series-rated combination between the fuse and breaker, not just fuse sizing based on let-through energy."
Would the breakers in the manufactured rack mounted PDU need to be considered under this article? Its a 50amp 14.4 kW rPDU with 6 branch circuit breakers.
"Long story short, the rPDUs we have 5KA rated breakers within them and I'm needing to reduce the fault current to an acceptable level from my busway.
To reduce fault current to a level acceptable for the PDU breakers, I planned to use a Bussmann fuse upstream. However, since the breakers are active components, I understand that NEC 240.86 requires a tested and listed series-rated combination between the fuse and breaker, not just fuse sizing based on let-through energy."
Would the breakers in the manufactured rack mounted PDU need to be considered under this article? Its a 50amp 14.4 kW rPDU with 6 branch circuit breakers.