NEC 240.2 gives a definition for a curren-limiting overcurrent protective device and the commentary in the handbook eludes that its purpose is to cut off a fault current in less than one-half cycle, thus preventing fault currents from building up to their full avaiable values.
NEC 240.86 requires series rating for circuit breakers used on a circuit having an available fault current higher than it's marked rating.
I interperated this to mean that if the let-thru value after the system's main disconnect is more than the down stream distribution's marked rating then the system must be fully or series rated for the aviable fault-current before the main. However, if the the let-thru value after the system's main disconnect is less than the down stream distribution's marked rating then series rating is not required.
The city of Denver has interperted 240.86 to mean that electrical systems will be fully or series rated reguardless of let-thru fault current values.
If this is the case then what is the purpose of Current-Limiting Overcurrent Protective Devices?
Am I missing something or is the City off on it's enforcement?
NEC 240.86 requires series rating for circuit breakers used on a circuit having an available fault current higher than it's marked rating.
I interperated this to mean that if the let-thru value after the system's main disconnect is more than the down stream distribution's marked rating then the system must be fully or series rated for the aviable fault-current before the main. However, if the the let-thru value after the system's main disconnect is less than the down stream distribution's marked rating then series rating is not required.
The city of Denver has interperted 240.86 to mean that electrical systems will be fully or series rated reguardless of let-thru fault current values.
If this is the case then what is the purpose of Current-Limiting Overcurrent Protective Devices?
Am I missing something or is the City off on it's enforcement?