Does it need to be one 2/0 copper ground or I can use (3)#2 cu? means one #2 each parallel. thank you250.102(C). Also #2 is not large enough. You need a 2/0 copper or 4/0 aluminum. The total kcmil of your conductors is 750 kcmil.
There needs to be a full sized (2/0 in this case) ground in every conduit of a parallel set.Does it need to be one 2/0 copper ground or I can use (3)#2 cu? means one #2 each parallel. thank you
This appears to be a supply side bonding jumper and, unlike an EGC, only needs to be sized for the ungrounded conductors that it is installed with.There needs to be a full sized (2/0 in this case) ground in every conduit of a parallel set.