K ka6chp Member Dec 4, 2004 #1 GENTLEMEN: IN RE NEC 250.122 (B), IF I GO FROM 12 AWG TO 10 AWG TO COMPENSATE FOR VOLTAGE DROP (ON SOME EXTERIOR LIGHTING), DO I ALSO HAVE TO INCREASE THE GROUNDING/BONDING WIRE FROM 12 TO 10? THE BREAKER IS 20 AMPS. THANKS.
GENTLEMEN: IN RE NEC 250.122 (B), IF I GO FROM 12 AWG TO 10 AWG TO COMPENSATE FOR VOLTAGE DROP (ON SOME EXTERIOR LIGHTING), DO I ALSO HAVE TO INCREASE THE GROUNDING/BONDING WIRE FROM 12 TO 10? THE BREAKER IS 20 AMPS. THANKS.
George Stolz Moderator Staff member Location Windsor, CO NEC: 2023 Occupation Hospital Master Electrician Dec 4, 2004 #2 Re: NEC 250.122 (B) That's an awesome question! To which...uh... Since 250.122 is based on the OCPD, I'd say that the ground doesn't change. But that's my guess.
Re: NEC 250.122 (B) That's an awesome question! To which...uh... Since 250.122 is based on the OCPD, I'd say that the ground doesn't change. But that's my guess.
B bphgravity Senior Member Location Florida Dec 4, 2004 #3 Re: NEC 250.122 (B) Yes, the equipment grounding conductor must also be increased. The real question is when you go from say #10 to #6 Both would generally only require a #10 egc, yet the section doesn't give an exceptions. [ December 04, 2004, 09:53 PM: Message edited by: bphgravity ]
Re: NEC 250.122 (B) Yes, the equipment grounding conductor must also be increased. The real question is when you go from say #10 to #6 Both would generally only require a #10 egc, yet the section doesn't give an exceptions. [ December 04, 2004, 09:53 PM: Message edited by: bphgravity ]
K kiloamp7 Senior Member Dec 4, 2004 #4 Re: NEC 250.122 (B) bphgravity is correct & has a good point on the # 6. You could maybe think of a 60A ckt. & the fact that EGC of # 10 is okay for it. Earlier NEC's, such as 250-95 in '96 Code, actually spoke of adjusting size for voltage drop .
Re: NEC 250.122 (B) bphgravity is correct & has a good point on the # 6. You could maybe think of a 60A ckt. & the fact that EGC of # 10 is okay for it. Earlier NEC's, such as 250-95 in '96 Code, actually spoke of adjusting size for voltage drop .
charlie b Moderator Staff member Location Lockport, IL Occupation Semi-Retired Electrical Engineer Dec 5, 2004 #5 Re: NEC 250.122 (B) Originally posted by ka6chp: GENTLEMEN: Click to expand... Let's give equal consideration to the ladies who are members of this Forum. Also, please drop the ALL CAPS.
Re: NEC 250.122 (B) Originally posted by ka6chp: GENTLEMEN: Click to expand... Let's give equal consideration to the ladies who are members of this Forum. Also, please drop the ALL CAPS.