I read the above NEC section and I see a problem with the language. It states:
Equipment grounding conductors run with feeder taps shall not be smaller than shown in Table 250.122 based on the rating of the overcurrent device ahead of the feeder but shall not be required to be larger than the tap conductors.
Let us assume a 10 foot tap with the feeder protected at 150A. According to NEC 240 10 ft taps can have an ampacity as low as 1/10 of the rating of the OCPD which in this example would be 15A. Here's the problem if you size the EGC to 15A ampacity it would violate the first part of the above stated rule where it state's that the EGC cannot be smaller than shown in NEC Table 250.122. So why does it say that the EGC is not required to be larger than the tap conductors? It would certainly have to be larger in this case.
Equipment grounding conductors run with feeder taps shall not be smaller than shown in Table 250.122 based on the rating of the overcurrent device ahead of the feeder but shall not be required to be larger than the tap conductors.
Let us assume a 10 foot tap with the feeder protected at 150A. According to NEC 240 10 ft taps can have an ampacity as low as 1/10 of the rating of the OCPD which in this example would be 15A. Here's the problem if you size the EGC to 15A ampacity it would violate the first part of the above stated rule where it state's that the EGC cannot be smaller than shown in NEC Table 250.122. So why does it say that the EGC is not required to be larger than the tap conductors? It would certainly have to be larger in this case.