1/ The code says: "Where metal fences are located within 5 m (16 ft) of the exposed electrical conductors or equipment, the fence shall be bonded to the grounding electrode system with wire-type bonding jumpers". What is the "grounding electrode system"?
If I connect the fence to many ground rods, should all the ground rods to be connected together? or is it OK if all the rods are not connected together?
If all the rods must connected together, should all the ground rods also connect to the ground ring in the equipment pad?
2/ The code says "Where metal fences are located within 5 m (16 ft) of the exposed electrical conductors or equipment," then the "Bonding jumpers shall be installed at each fence corner and at maximum 50 m (160 ft) intervals along the fence."
For example of a rectangular fence ABCD, if there is only 1 place in AB side where the exposed conductor is within 16ft, then should we ground the whole fence with 160ft interval? or should we just ground the fence in only 1 side of AB to the corners of A and B (the other side of BC, CD, and DA will not be grounded)?
In the case that the AB side is so long, for example 1000', should we have to ground all the length or when to stop?
3/ The code says "Where bare overhead conductors cross the fence, bonding jumpers shall be installed on each side of the crossing."
How far away the bonding jumper to be install from each side of the crossing? 5ft or 10ft or what?
When grounding the fence with overhead line crossing, when should we stop grounding (160ft from each side of the crossing?) or we have to ground the whole fence?
Thank you very much.
If I connect the fence to many ground rods, should all the ground rods to be connected together? or is it OK if all the rods are not connected together?
If all the rods must connected together, should all the ground rods also connect to the ground ring in the equipment pad?
2/ The code says "Where metal fences are located within 5 m (16 ft) of the exposed electrical conductors or equipment," then the "Bonding jumpers shall be installed at each fence corner and at maximum 50 m (160 ft) intervals along the fence."
For example of a rectangular fence ABCD, if there is only 1 place in AB side where the exposed conductor is within 16ft, then should we ground the whole fence with 160ft interval? or should we just ground the fence in only 1 side of AB to the corners of A and B (the other side of BC, CD, and DA will not be grounded)?
In the case that the AB side is so long, for example 1000', should we have to ground all the length or when to stop?
3/ The code says "Where bare overhead conductors cross the fence, bonding jumpers shall be installed on each side of the crossing."
How far away the bonding jumper to be install from each side of the crossing? 5ft or 10ft or what?
When grounding the fence with overhead line crossing, when should we stop grounding (160ft from each side of the crossing?) or we have to ground the whole fence?
Thank you very much.