NEC 2017 section 250.24(A)(1) the grounding electrode conductor connection shall be made at any accessible point from load end of the overhead service conductors, service drops, unground service conductors, or service lateral to including the terminal or bus to which the grounded service conductor is connected at the service disconnecting means.
My question is lets say grounding electrode conductor is made at service disconnecting means and its a 2000A 480/277V three phase switchboard. This mean that the grounding electrode conductor needs to be connected to neutral bar. Does this mean one needs to drill neutral bar to connect grounding electrode conductor or not? Does anyone know?
My question is lets say grounding electrode conductor is made at service disconnecting means and its a 2000A 480/277V three phase switchboard. This mean that the grounding electrode conductor needs to be connected to neutral bar. Does this mean one needs to drill neutral bar to connect grounding electrode conductor or not? Does anyone know?