I am working on a project where the owner has generators connected through a distribution switchboard that feeds multiple ATS's as a non-separately derived system. The existing ATS's are all 3 pole. The generators are reaching end-of-life and they would like to install new generators (building exterior) connected through a new generator distribution switchboard in an adjacent building, back-feed the existing generator distribution switchboard, and backup the adjacent building's service from the same generators.
As the existing ATS's in Building #1 are 3 pole, the new generators will not have a neutral-ground bond.
If the new ATS in Building #2 is also 3 pole, the neutrals of the 2 services would be ties together. Is this a violation of 250.24(A)(5)?
Can the new ATS in Building #2 be 4 pole with a switched neutral, making the distribution section of Building #2's service switchboard a separately derived system with the neutral-ground bond at Building #2's service disconnect when the ATS is in Normal position, and the neutral-ground bond at Building #1's service disconnect when the ATS is in Emergency position?
As the existing ATS's in Building #1 are 3 pole, the new generators will not have a neutral-ground bond.
If the new ATS in Building #2 is also 3 pole, the neutrals of the 2 services would be ties together. Is this a violation of 250.24(A)(5)?
Can the new ATS in Building #2 be 4 pole with a switched neutral, making the distribution section of Building #2's service switchboard a separately derived system with the neutral-ground bond at Building #2's service disconnect when the ATS is in Normal position, and the neutral-ground bond at Building #1's service disconnect when the ATS is in Emergency position?