If you have a non-utility owned pad mounted outdoor transformer does 250.30(A)(1) Exception No. 2 and 250.30(A)(2) Exception allow you to treat the bonding connections with the transformer and the first disconnect as you would a utility owned transformer? i.e. no bonding jumper is allowed.
The wording "...a system bonding jumper at both the source and the first disconnecting means shall be permitting if doing so does not establish a parallel path for the ground conductor." Does "at both" simply mean between?
Thanks,
WK
The wording "...a system bonding jumper at both the source and the first disconnecting means shall be permitting if doing so does not establish a parallel path for the ground conductor." Does "at both" simply mean between?
Thanks,
WK