Hi Folks,
I have an Separately Derived System installation in which a an alternate source, stand-by generator, feeds a switchboard via a 4-pole transfer switch. Article 250 mentions "first disconnecting means" several times. Does this refer to the transfer switch or a Mains in the switchboard? My understanding is that this refers to the Main breaker in the Switchboard downstream of the transfer switch. If so, a system bonding jumper can also be installed(retained) in the switchboard if existing so that the grounded conductor from the switchboard back to the transfer switch is permitted to serve as ground-fault return path per 250.32(B)(1) Exceptions 1&2.
My understanding further is that the EGC from the Generator to the MTS will act as a supply-side bonding jumper, am I correct here?
Thank you for your feedback.
Regards,
EE
I have an Separately Derived System installation in which a an alternate source, stand-by generator, feeds a switchboard via a 4-pole transfer switch. Article 250 mentions "first disconnecting means" several times. Does this refer to the transfer switch or a Mains in the switchboard? My understanding is that this refers to the Main breaker in the Switchboard downstream of the transfer switch. If so, a system bonding jumper can also be installed(retained) in the switchboard if existing so that the grounded conductor from the switchboard back to the transfer switch is permitted to serve as ground-fault return path per 250.32(B)(1) Exceptions 1&2.