erickench
Senior Member
- Location
- Brooklyn, NY
I look at these two NEC rules and I see a potential conflict. 250.32(A)Exception state's the following:
A grounding electrode shall not be required
where only a single branch circuit, including a multiwire
branch circuit, supplies the building or structure and the
branch circuit includes an equipment grounding conductor
for grounding the normally non?current-carrying metal
parts of equipment.
But immediately following 250.32(B)(1) state's something different:
An equipment grounding conductor as described in 250.118 shall be
run with the supply conductors and be connected to the building or structure disconnecting means and to the
grounding electrode(s).
I assume in the first case that if there's a ground wire then a grounding electrode is not needed. But in the second case I guess they mean a continuous metal raceway that is bonded would have to be connected to a grounding electrode. Otherwise the two rules conflict.
A grounding electrode shall not be required
where only a single branch circuit, including a multiwire
branch circuit, supplies the building or structure and the
branch circuit includes an equipment grounding conductor
for grounding the normally non?current-carrying metal
parts of equipment.
But immediately following 250.32(B)(1) state's something different:
An equipment grounding conductor as described in 250.118 shall be
run with the supply conductors and be connected to the building or structure disconnecting means and to the
grounding electrode(s).
I assume in the first case that if there's a ground wire then a grounding electrode is not needed. But in the second case I guess they mean a continuous metal raceway that is bonded would have to be connected to a grounding electrode. Otherwise the two rules conflict.