NEC 250.32 (A) Exception & 250.32(B)(1)

Status
Not open for further replies.

erickench

Senior Member
Location
Brooklyn, NY
I look at these two NEC rules and I see a potential conflict. 250.32(A)Exception state's the following:

A grounding electrode shall not be required
where only a single branch circuit, including a multiwire
branch circuit, supplies the building or structure and the
branch circuit includes an equipment grounding conductor
for grounding the normally non?current-carrying metal
parts of equipment.

But immediately following 250.32(B)(1) state's something different:

An equipment grounding conductor as described in 250.118 shall be
run with the supply conductors and be connected to the building or structure disconnecting means and to the
grounding electrode(s).

I assume in the first case that if there's a ground wire then a grounding electrode is not needed. But in the second case I guess they mean a continuous metal raceway that is bonded would have to be connected to a grounding electrode. Otherwise the two rules conflict.
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
I look at these two NEC rules and I see a potential conflict. 250.32(A)Exception state's the following:

A grounding electrode shall not be required
where only a single branch circuit, including a multiwire
branch circuit, supplies the building or structure and the
branch circuit includes an equipment grounding conductor
for grounding the normally non?current-carrying metal
parts of equipment.

But immediately following 250.32(B)(1) state's something different:

An equipment grounding conductor as described in 250.118 shall be
run with the supply conductors and be connected to the building or structure disconnecting means and to the
grounding electrode(s).

I assume in the first case that if there's a ground wire then a grounding electrode is not needed. But in the second case I guess they mean a continuous metal raceway that is bonded would have to be connected to a grounding electrode. Otherwise the two rules conflict.

Eric, we are looking at the difference between a feeder and a mwbc. In case one you could run a 12/3 with ground (doesn't have to be #12) and install a main disco at the building and install a DP breaker at the source and you are good to go.

In case 2 we are looking at a feeder to a panel regardless of the wiring method. DB, PVC etc-- they all require potential 2 rods unless you meet the 25 ohm rule or have an CCE installed or other acceptable means.
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
Eric, we are looking at the difference between a feeder and a mwbc. In case one you could run a 12/3 with ground (doesn't have to be #12) and install a main disco at the building and install a DP breaker at the source and you are good to go.

In case 2 we are looking at a feeder to a panel regardless of the wiring method. DB, PVC etc-- they all require potential 2 rods unless you meet the 25 ohm rule or have an CCE installed or other acceptable means.


And I agree with Dennis.

Roger
 

erickench

Senior Member
Location
Brooklyn, NY
You know what? I just looked at 250.32(D)(2). It say's something about a building being supplied by more than one branch circuit. Therefore the heading of 250.32(B) could mean a feeder going into a panelboard and then branch circuits are coming out of it. If a building is supplied by a branch circuit only and not a feeder then no grounding electrode is required provided there is a ground wire. But if there is feeder going into a panelboard with branch circuits coming out then you would need a grounding electrode.:)
 

ceb58

Senior Member
Location
Raeford, NC
You know what? I just looked at 250.32(D)(2). It say's something about a building being supplied by more than one branch circuit. Therefore the heading of 250.32(B) could mean a feeder going into a panelboard and then branch circuits are coming out of it. If a building is supplied by a branch circuit only and not a feeder then no grounding electrode is required provided there is a ground wire. But if there is feeder going into a panelboard with branch circuits coming out then you would need a grounding electrode.:)

You know what? Your correct:D
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
If a building is supplied by a branch circuit only and not a feeder then no grounding electrode is required provided there is a ground wire. But if there is feeder going into a panelboard with branch circuits coming out then you would need a grounding electrode.:)

By George, I think you've got it. :)

Roger
 

erickench

Senior Member
Location
Brooklyn, NY
It's just the way it's written. They should clarify that the branch circuits are either supplying a building or are coming out of a panelboard.
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
It's just the way it's written. They should clarify that the branch circuits are either supplying a building or are coming out of a panelboard.

I would advise reading the def. of branch circuit and feeder. I am not sure I understand your above statement. A branch cir. can feed the detached building from a panelboard and not connect to any other panelboard. If it connects to a panelboard in the detached structure then that wire is no longer a branch cir but has now become a feeder.

It seems quite clear so I was wondering if I was missing something more.
 

iwire

Moderator
Staff member
Location
Massachusetts
It's just the way it's written. They should clarify that the branch circuits are either supplying a building or are coming out of a panelboard.

I have no idea what you mean. :-? The panelboard has nothing to do with it.

If you have a separate structure that is supplied by a feeder (see article 100) there must be a grounding electrode system located at the separate structure.



If you have a separate structure that is supplied by a branch circuit (see article 100) we are not required to have a grounding electrode system located at the separate structure.

A multi-wire branch circuit can be considered one circuit.
 