ramsy
Roger Ruhle dba NoFixNoPay
- Location
- LA basin, CA
- Occupation
- Service Electrician 2020 NEC
It appears NEC 250.32(B)(2) advocates an electrocution hazard in all code cycles, including the 2008 exception for existing premises.
Where no EGC exists at loadside feeders NEC instructs contractors to bond neutral for fault-current path, as long as no objectionable current flows.
So anyone --like soldiers in Iraq-- that touch this bootlegged equipment to plumbing fixture can be electrocuted. As loads charge EGC's with neutral current in subpanel, GFCI mechanisms are defeated by parallel paths of people shorting electrical-equipment housings to the common-plumbing grid.
Where no EGC exists at loadside feeders NEC instructs contractors to bond neutral for fault-current path, as long as no objectionable current flows.
The electrocution potential exists --without objectionable current flow-- when separate-structure-plumbing grids bond to primary services.250.32(B)(2) said:..there are no continuous metallic paths bonded to the grounding system in each building
So anyone --like soldiers in Iraq-- that touch this bootlegged equipment to plumbing fixture can be electrocuted. As loads charge EGC's with neutral current in subpanel, GFCI mechanisms are defeated by parallel paths of people shorting electrical-equipment housings to the common-plumbing grid.