We have many vendor-supplied cabinets (from Italy) with two ground buses at the base of the enclosure: one is labeled PE (plant earth) and the other is labeled SH (shield), which is mounted on phenolic 'isolators'.
A vendor supplied, blue jacketed #6 AWG bonding jumper connects the two buses together - the cabinet has 480V devices (CB/OL devices) and Allen Bradley PLC, with analog and discreet I/O cards. I want to remove the blue bonding jumper, so I don't introduce noise (EMI) into the instrumentation circuitry. But NEC 250.50 requires the two systems to be bonded together. How do I protect my 4-20mA, millivolt and digital circuits from EMI and satisfy the NEC at the same time?
A vendor supplied, blue jacketed #6 AWG bonding jumper connects the two buses together - the cabinet has 480V devices (CB/OL devices) and Allen Bradley PLC, with analog and discreet I/O cards. I want to remove the blue bonding jumper, so I don't introduce noise (EMI) into the instrumentation circuitry. But NEC 250.50 requires the two systems to be bonded together. How do I protect my 4-20mA, millivolt and digital circuits from EMI and satisfy the NEC at the same time?