NEC 250.66 Transformer Grounding Bar

Status
Not open for further replies.

bcnj

Member
Location
NYC
I am on a project where we are installing appx. 10 30kva-65kva transformers fed from one distribution panel. All transformers GEC will be tied into a single Grounding Bar that goes to building steel. Am I correct in saying the GEC sizing to the ground at should be the sum of all 10 GEC's to the transformers?


Sent from my iPhone using Tapatalk
 
I agree with Bob #3/0 is the minimum and the maximum required for a common grounding electrode that serves more than one transformer.
 
So even if I had 100 30kva transformers it will still be a 3/0?

I am thinking it 250.66 Note#1 is applicable.

Notes:
1. Where multiple sets of service-entrance conductors are used as permitted in 230.40, Exception No. 2, the equivalent size of the largest service-entrance conductor shall be determined by the largest sum of the areas of the corresponding conductors of each set.


Sent from my iPhone using Tapatalk
 
So even if I had 100 30kva transformers it will still be a 3/0?

I am thinking it 250.66 Note#1 is applicable.

Notes:
1. Where multiple sets of service-entrance conductors are used as permitted in 230.40, Exception No. 2, the equivalent size of the largest service-entrance conductor shall be determined by the largest sum of the areas of the corresponding conductors of each set.


Sent from my iPhone using Tapatalk

You would still end up with a 3/0
 
So even if I had 100 30kva transformers it will still be a 3/0?

I am thinking it 250.66 Note#1 is applicable.

Notes:
1. Where multiple sets of service-entrance conductors are used as permitted in 230.40, Exception No. 2, the equivalent size of the largest service-entrance conductor shall be determined by the largest sum of the areas of the corresponding conductors of each set.


Sent from my iPhone using Tapatalk

Not applicable:

Is these transformers are fed from a distribution panel the secondaries would not be service conductors.
Note 1 applies to parallel condcutors (connected together at both ends)
 
You are getting the size of the EGC based off of table 250.66. The table is labeled for service conductors.

Also, in theory, can someone argue that there is or is no limit to the amount you can place in a 3/0 wire?


Sent from my iPhone using Tapatalk
 
You are getting the size of the EGC based off of table 250.66. The table is labeled for service conductors.

Also, in theory, can someone argue that there is or is no limit to the amount you can place in a 3/0 wire?


Sent from my iPhone using Tapatalk
ECGs are never sized using Table 250.66.
 
Except 250.66 Note 1

Notes:
1. Where multiple sets of service-entrance conductors are used as permitted in 230.40, Exception No. 2, the equivalent size of the largest service-entrance conductor shall be determined by the largest sum of the areas of the corresponding conductors of each set.



Sent from my iPhone using Tapatalk
 
Add the Circular Mils for each GEC and make sure your main GEC is equal or greater.


Sent from my iPhone using Tapatalk
 
Except 250.66 Note 1

Notes:
1. Where multiple sets of service-entrance conductors are used as permitted in 230.40, Exception No. 2, the equivalent size of the largest service-entrance conductor shall be determined by the largest sum of the areas of the corresponding conductors of each set.
You cannot exceed "Over 1100" or "Over 1750". :huh:
 