NEC 250.8

Status
Not open for further replies.

hhsting

Senior Member
Location
Glen bunie, md, us
Occupation
Junior plan reviewer
Can the following connector be used to connect and bond equipment grounding conductor to the trough bus bar inside trough? is it NEC 2014 or NEC 2014 section 250.8 code compliant or not?

 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Lay-in style lugs are used for that application all of the time. That would fall under 250.8(A)(1).
 

hhsting

Senior Member
Location
Glen bunie, md, us
Occupation
Junior plan reviewer
Lay-in style lugs are used for that application all of the time. That would fall under 250.8(A)(1).

I heard that pass through lug one attach post #1 attachment is extremely hard to apply proper torque to without the lug turning on bus bar. Is that correct or incorrect?
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
I heard that pass through lug one attach post #1 attachment is extremely hard to apply proper torque to without the lug turning on bus bar. Is that correct or incorrect?
You could grab the lug with small Channellocks while tightening.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
I heard that pass through lug one attach post #1 attachment is extremely hard to apply proper torque to without the lug turning on bus bar. Is that correct or incorrect?
As Larry gave you one method the answer is no not really.
 