There was a change in the 2008 NEC which is now being used by New York. The above NEC section state's the following:
Metal enclosures and raceways for service conductors and equipment shall be connected to the grounded system conductor if the electrical system is grounded or to the grounded electrode conductor for electrical systems that are not grounded.
I am assuming that this applies to the case where meter enclosures are neutral bonded when they come from the factory. Is that the purpose of this rule?
Metal enclosures and raceways for service conductors and equipment shall be connected to the grounded system conductor if the electrical system is grounded or to the grounded electrode conductor for electrical systems that are not grounded.
I am assuming that this applies to the case where meter enclosures are neutral bonded when they come from the factory. Is that the purpose of this rule?