OK, new questions, different code section. Inspector said we need a 4/0 to a (N) isolated ground rod for a (N) MV LBS. The (N) MV LBS is installed in the same electrical room, next to (E) MV starters and is connected to the (E) MV SWGR ground bus by a #1 conductor. The (N) LBS is connected to the utility side of the MV SWGR and is the disconnect for a dedicated transformer (2400/480v, 3Ph, 750kVA) that feeds a fire pump (N). Same arrangement as an (E) LBS at the other end of the MV SWGR. Perhaps I am reading article 250 / 490 wrong. The other question, why have a separate, isolate ground rod, why not just tie it to the existing ground grid outside the building if I need a separate bonding conductor for this (N) MV LBS. Can I connect the (N) LBS ground bus bar to the (E) SWGR ground bus with 4/0 instead?